Garage grounding and bonding questions.

Status
Not open for further replies.
Hello I have a 3 wire overhead line coming from the house which comes from the service on its own 70 amp disconnect.

The garage had fuses and now has a breaker panel, so I have the two hots and the neutral/ground coming into the box from the service disconnect.

The neutral bus has the ground from the service, and there is an optional lug to bond the neutral bus and ground together.
I assume I use the lug when I have an old 3 wire service coming in but I was not sure.

If the housing wiring gets redone and changed to a 4 wire garage service do I separate the two and run a wire (green) to the ground bus and a wire (white) to the neutral bus?


Part 2

The garage did not have any sort of grounding actually running to the ground so I have bought two 8 foot grounding rods and #6 bare wire to run from the rods to the ground bus in the panel.

Are there spacing requirements for separating the two grounding rods from each other?

Do they have to be driven into the ground vertically or can I dig two trenches and lay them horizontally next to the slab?
 

DrSparks

The Everlasting Know-it-all!
Location
Madison, WI, USA
Occupation
Master Electrician and General Contractor
You are allowed to reground the neutral bus for existing installations only. If you replace the wiring from the house to the garage you must run a 4-wire circuit with a ground sized according to Table 250.122.

The ground rods must be spaced 8 feet apart at a minimum but the further apart you place them the better.

If there are any common metal systems between the garage and the house such as metal water pipes it is absolutely imperative that the neutral be isolated from the equipment ground and a new feeder run from the house with a dedicated equipment ground. If there are parallel paths for the neutral current to return to the service then neutral current will be present on the equipment ground.

The ground rods are allowed to be buried in a trench horizontally only if it is impossible to drive them in vertically. You will get suboptimal results by laying them in a trench rather than driving them in.
 

GerryB

Senior Member
You are allowed to reground the neutral bus for existing installations only. If you replace the wiring from the house to the garage you must run a 4-wire circuit with a ground sized according to Table 250.122.

The ground rods must be spaced 8 feet apart at a minimum but the further apart you place them the better.

If there are any common metal systems between the garage and the house such as metal water pipes it is absolutely imperative that the neutral be isolated from the equipment ground and a new feeder run from the house with a dedicated equipment ground. If there are parallel paths for the neutral current to return to the service then neutral current will be present on the equipment ground.

The ground rods are allowed to be buried in a trench horizontally only if it is impossible to drive them in vertically. You will get suboptimal results by laying them in a trench rather than driving them in.
6' min on the rods (mis spoke?) But are you saying if existing rigid conduit with 3 conductors you can't reuse it?
 

DrSparks

The Everlasting Know-it-all!
Location
Madison, WI, USA
Occupation
Master Electrician and General Contractor
you could use rigid conduit as the equipment grounding conductor.
I apologize. The code minimum is 6 feet. I always use the length of a ground rod as a meter to space my ground rods apart. But it still stands that the further apart do you place them the lower the impedance to ground you will have.

If you have buried ferrous metal conduit then there's a good chance that the conduit has long rotted away. I would not rely on the Conduit as an equipment ground. I would be amazed if you were able to pull new wire through the existing conduit and if you were able to I'm sure it would be caked with mud and rust.

Sent from my A574BL using Tapatalk
 

DrSparks

The Everlasting Know-it-all!
Location
Madison, WI, USA
Occupation
Master Electrician and General Contractor
I apologize. The code minimum is 6 feet. I always use the length of a ground rod as a meter to space my ground rods apart. But it still stands that the further apart do you place them the lower the impedance to ground you will have.

If you have buried ferrous metal conduit then there's a good chance that the conduit has long rotted away. I would not rely on the Conduit as an equipment ground. I would be amazed if you were able to pull new wire through the existing conduit and if you were able to I'm sure it would be caked with mud and rust.

Sent from my A574BL using Tapatalk

Also it is also common practice to run PVC underground and then transition to RMC as it emerges from grade. This would obviously interrupt ground continuity of the pipe.

Sent from my A574BL using Tapatalk
 

DrSparks

The Everlasting Know-it-all!
Location
Madison, WI, USA
Occupation
Master Electrician and General Contractor
I left emoticons out because it's a legitimate question, albeit presented in a smart alecky way. What performance of two measly 5/8" ground rods is lost if the rods are laying in a trench?
You make a good point. The difference in performance as far as lower impedance to Earth ground is miniscule but when the ground rods are driven into compacted soil rather than being lain in a trench and Loosely covered with soil. Even if you use a tamper to compact the soil you still not achieve optimal results

Sent from my A574BL using Tapatalk
 

kwired

Electron manager
Location
NE Nebraska
You make a good point. The difference in performance as far as lower impedance to Earth ground is miniscule but when the ground rods are driven into compacted soil rather than being lain in a trench and Loosely covered with soil. Even if you use a tamper to compact the soil you still not achieve optimal results

Sent from my A574BL using Tapatalk
I can agree that it will usually result in lower impedance, but it matters because...

it makes the "dirt worshippers" happy?
 
I appreciate the replies and the discussion that has ensued, my question has been answered thoroughly.

There are no shared metal systems, like pipes, between the garage and the house.
The only connection is the overhead wire which is existing and will not be rewired until I get the gumption up to do the house.

The garages cement slab on the wall with the panel is 24 feet wide but there is a sidewalk and fence part way, I could space the rods out at most 20 feet if this gives me better grounding then I will do so, with them being driven vertically.

If 20 feet is crazy wide I could space them closer.

When I do eventually replace the feeder, would running it underground be a better option to the overhead wire, or is there no preference when both methods are an option?
 
Last edited:

kwired

Electron manager
Location
NE Nebraska
I appreciate the replies and the discussion that has ensued, my question has been answered thoroughly.

There are no shared metal systems, like pipes, between the garage and the house.
The only connection is the overhead wire which is existing and will not be rewired until I get the gumption up to do the house.

The garages cement slab on the wall with the panel is 24 feet wide but there is a sidewalk and fence part way, I could space the rods out at most 20 feet if this gives me better grounding then I will do so, with them being driven vertically.

If 20 feet is crazy wide I could space them closer.

When I do eventually replace the feeder, would running it underground be a better option to the overhead wire, or is there no preference when both methods are an option?
Code wise there is no preference.

Appearance wise, underground is always a cleaner look.
 