Is there a Code or standard that stipulates a time period, within which the testing of Earth Resistance for an installation must be carried out to see whether the earthing system is working or not??
Since the NEC does not specify any direct performance metrics for a building Ground Electrode System (GES) it also says nothing about testing.Is there a Code or standard that stipulates a time period, within which the testing of Earth Resistance for an installation must be carried out to see whether the earthing system is working or not??
Is there a Code or standard that stipulates a time period, within which the testing of Earth Resistance for an installation must be carried out to see whether the earthing system is working or not??
Since the NEC does not specify any direct performance metrics for a building Ground Electrode System (GES) it also says nothing about testing.
Other industry specific codes or manuals of good practice, such as those of the utilities (the NESC) and the Communications industry (a Motorola document?), may go into performance rather than just design specifications, but I am not familiar enough with them to relate them to your question.
Is there a Code or standard that stipulates a time period, within which the testing of Earth Resistance for an installation must be carried out to see whether the earthing system is working or not??
You posted your question on the wrong type of forum.
Your answers are found in the IEEE Green Book.
Here is good white paper on Earth grounding that may help you in finding the answers to your questions.
http://www.cpccorp.com/deep.htm
.
This paper utilizes field data taken from over 140 deep driven electrodes installed over a 5 year period in several states.
You posted your question on the wrong type of forum.
Your answers are found in the IEEE Green Book.
Here is good white paper on Earth grounding that may help you in finding the answers to your questions.
http://www.cpccorp.com/deep.htm
.
.... Must be the deep earth grounding :roll:
How important is that in relationship to the triangle?
That's putting it mildly. :thumbsup:I know them. Another one of these scam "grounding expert" companies. Nothing but nonsense.
Do you really believe that nonsense and being a scam?That's putting it mildly. :thumbsup:
Roger
Do you really believe that nonsense and being a scam?
Do you really believe that nonsense and being a scam?
Since you are (obviously)
one of those non-believers, albeit insulting , why do companies pay grounding engineer specialists over a $100,000 a year salary.
Do you make over 100K/year wearing a pouch with Klein's and screwdriver?
If not, and you are moonlighting as a PE that knows more about grounding and your take home pay doesn't come close to100K, there is an opening for experts like you at: Sandia National Laboratory in Livermore CA. A research lab.
Give it a shot and show us what you got.
As a footnote: give them respect, it will make you look good--and this site as well.
I didn't till you re-mentioned it. I'd laugh out loud it I wasn't so disgusted by this mentality.Have you read the page linked to in post #6?
CASE STUDY 2
The facility had a history of equipment problems and failures as well as complaints by employees of electrical shock....
A deep driven electrode system was selected as the best solution for this site.....
Pretty much.Do you really believe that nonsense and being a scam?
Foolish I guess.Since you are (obviously)
one of those non-believers, albeit insulting , why do companies pay grounding engineer specialists over a $100,000 a year salary.
My salary didn't include wearing a pouch.Do you make over 100K/year wearing a pouch with Klein's and screwdriver?
They're to late, I'm retired.If not, and you are moonlighting as a PE that knows more about grounding and your take home pay doesn't come close to100K, there is an opening for experts like you at: Sandia National Laboratory in Livermore CA. A research lab.
Give it a shot and show us what you got.
As a footnote: give them respect, it will make you look good--and this site as well.
In order to understand earth grounding and test procedures, it is necessary to review why grounding is important. The list below gives some of the basic requirements of an effective ground system.
limits voltage in a electrical distribution system to definite fixed values limits voltage to within insulation ratings provides a more stable system with a minimum of transient over voltage and electrical noise provides a path to ground in fault conditions for quick isolation of equipment with operation of ground fault protection provides grounding of all conductive enclosures that may be touched by personnel, thereby eliminating shock hazards reduces static electricity that may be generated within facilities
I did not go to any links posted, I will say there often is too much emphasis put on "earthing", especially on the average home or place of business.Do you really believe that nonsense and being a scam?
Since you are (obviously)
one of those non-believers, albeit insulting , why do companies pay grounding engineer specialists over a $100,000 a year salary.
Do you make over 100K/year wearing a pouch with Klein's and screwdriver?
If not, and you are moonlighting as a PE that knows more about grounding and your take home pay doesn't come close to100K, there is an opening for experts like you at: Sandia National Laboratory in Livermore CA. A research lab.
Give it a shot and show us what you got.
As a footnote: give them respect, it will make you look good--and this site as well.
Pretty much.
Foolish I guess.
My salary didn't include wearing a pouch.
They're to late, I'm retired.
Now, do you agree with what they say here?
Roger