250.24(A)(1) Bonding the grounded conductor.

Status
Not open for further replies.

AV8R

Member
Location
Kansas City
We work with multiple POCO's. One will have you bond the grounded conductor in the meter can, another will forbid it. My question is, if we are asked to bond the grounded conductor inside the meter can, are we still obligated to bond the grounded conductor at the main disconnect? Are we permitted to do it? Is it optional? 250.24(A)(1) seems to say it can be done at either location, to and including the the terminal or bus at the main. Am I interpreting that correctly to assume I need to still bond the neutral to the GEC at the main service disconnect?
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Most meter sockets are designed so that they automatically bond the grounded conductor due to the neutral "buss" being mounted to the can itself. 250.24 still requires you bond the service disconnect. Depending on the wiring method you may actually set up a "objectionable" current but this is accepted by practice.

Your question seems to be discussing the connection of a grounding electrode, not bonding. Unless POCO has a rule, that connection can be made at the meter or service disconnect. IMHO, the connection to a particular electrode should only originate at one of those locations to prevent objectionable flow (other electrodes can connection to the other location)
 

AV8R

Member
Location
Kansas City
Most meter sockets are designed so that they automatically bond the grounded conductor due to the neutral "buss" being mounted to the can itself. 250.24 still requires you bond the service disconnect. Depending on the wiring method you may actually set up a "objectionable" current but this is accepted by practice.

Your question seems to be discussing the connection of a grounding electrode, not bonding. Unless POCO has a rule, that connection can be made at the meter or service disconnect. IMHO, the connection to a particular electrode should only originate at one of those locations to prevent objectionable flow (other electrodes can connection to the other location)

I probably didn't ask the question correctly. We were asked by POCO to attach a grounding electrode to the meter can from a ground rod, and the neutral is also bonded to the meter can at that point. In addition, we still installed all of our grounding at the main disconnect; water main, building steel, concrete encased electrode, ETC. My foreman opted to leave out the bonding jumper between the neutral bar and the equipment ground, just like we would at a sub panel. I asked him to install the jumper at the main, after I inspected the panel. Now I'm second guessing myself and looking for confirmation or correction.
Thanks!
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I probably didn't ask the question correctly. We were asked by POCO to attach a grounding electrode to the meter can from a ground rod, and the neutral is also bonded to the meter can at that point. In addition, we still installed all of our grounding at the main disconnect; water main, building steel, concrete encased electrode, ETC. My foreman opted to leave out the bonding jumper between the neutral bar and the equipment ground, just like we would at a sub panel. I asked him to install the jumper at the main, after I inspected the panel. Now I'm second guessing myself and looking for confirmation or correction.
Thanks!

You were good up to the bold part. You need an MBJ at the panel.
 

AV8R

Member
Location
Kansas City
You were good up to the bold part. You need an MBJ at the panel.

That's what I thought, thanks. No matter how many grounding Continuing Ed classes I've taken, I feel like there's so much still to learn about a seemingly small subject, bonding and grounding.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
That's what I thought, thanks. No matter how many grounding Continuing Ed classes I've taken, I feel like there's so much still to learn about a seemingly small subject, bonding and grounding.
I read 250.64(A)(1) and GEC connection has to be accessible location. Utility meter can are locked by the utility and not accessible. Utility may be have special type of enclosure where GEC accessible otherwise GEC meter can wont be accessible.

Sent from my SM-G935U using Tapatalk
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I read 250.64(A)(1) and GEC connection has to be accessible location. Utility meter can are locked by the utility and not accessible. Utility may be have special type of enclosure where GEC accessible otherwise GEC meter can wont be accessible.
Not true, this is a common believed myth, a meter can is accessible or you could not have any connections inside it .

Roger
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Around here POCO locks the meter can so that no one steal power and meter is only accesible to POCO. I guess every POCO is different.

Sent from my SM-G935U using Tapatalk
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Around here POCO locks the meter can so that no one steal power and meter is only accesible to POCO. I guess every POCO is different.
That doesn't change the fact that it is still accessible, just an inconvenience to have to wait for them to get there.

Roger
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Defintion NEC accessible: capable of being reached quickly for operation, renewal, or inspections without requiring those to whom ready access is requisite to actions such as to use tools, to climb over or remove obstacles, or to resort to portable ladders and so forth.

One cannot reach quickly have to wait for POCO.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Defintion NEC accessible: capable of being reached quickly for operation, renewal, or inspections without requiring those to whom ready access is requisite to actions such as to use tools, to climb over or remove obstacles, or to resort to portable ladders and so forth.

One cannot reach quickly have to wait for POCO.
Go back and read Accessible (as applied to wiring methods), you're reading the wrong definition.

Roger
 
We work with multiple POCO's. One will have you bond the grounded conductor in the meter can, another will forbid it. My question is, if we are asked to bond the grounded conductor inside the meter can, are we still obligated to bond the grounded conductor at the main disconnect? Are we permitted to do it? Is it optional? 250.24(A)(1) seems to say it can be done at either location, to and including the the terminal or bus at the main. Am I interpreting that correctly to assume I need to still bond the neutral to the GEC at the main service disconnect?

I think the confusion is you are talking about two different things: one is the connection of the GEC to the grounded conductor, the other is the MBJ - the connection of the EGC bus to the grounded conductor.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Accessible: admitting close approach; not guarded by locked doors, elevation, or other effective means.

GEC connection applies to meter equipment enclosure.

Sent from my SM-G935U using Tapatalk
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I probably didn't ask the question correctly. We were asked by POCO to attach a grounding electrode to the meter can from a ground rod, and the neutral is also bonded to the meter can at that point. In addition, we still installed all of our grounding at the main disconnect; water main, building steel, concrete encased electrode, ETC. My foreman opted to leave out the bonding jumper between the neutral bar and the equipment ground, just like we would at a sub panel. I asked him to install the jumper at the main, after I inspected the panel. Now I'm second guessing myself and looking for confirmation or correction.
Thanks!

You did the right thing tell him to install the main bonding jumper. Having EGCs not ultimately connected to the grounded conductor is in my judgement a hundred times more dangerous than having the wrong location for connection of a grounding electrode conductor.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Accessible: admitting close approach; not guarded by locked doors, elevation, or other effective means.

GEC connection applies to meter equipment enclosure.

Sent from my SM-G935U using Tapatalk
You're still reading the wrong definition, read the one I pointed you to. After that if you still can't grasp it tell me why the other conductors landed in the meter can don't need to be accessible.

Just to help you out a little, most commercial buildings (hospitals, shopping centers, schools, etc...) have the electrical rooms locked which takes you away from the definition for Accessible which mean you need to look at Accessible (as applied to wiring methods)

Roger
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I dont know about other conductors being accessible but 250.24(A)(1) says GEC connection to be accessible.

Why would one use accessible as applied to wiring methods as oppose to accessible as applied to equipment? One needs access to inside meter where GEC is connected.

Sent from my SM-G935U using Tapatalk
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I dont know about other conductors being accessible but 250.24(D) says GEC connection to ne accessible.
All the conductors in a meter can are accessible period, whether or not some clueless POCO has their own rules does not change the NEC definition of
Accessible (as applied to wiring methods).

Why would one use accessible as applied to wiring methods as oppose to accessible as applied to equipment?
Because the wiring in the can is "wiring"

One needs access to inside meter where GEC is connected.
After being in the trade for more than 40 years I don't know of one single time a GEC needed attention inside a meter can.

Roger
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Alright. Just wondering under what circumstances one would use as accessible applied to equipment. Every equipment person wants access to need acces to wiring inside. Why is it even in code.
 