There may be multiple code-compliant ways to ground these. What are your opinions on best practices? I want to consider code compliance, and also just whatever electricians & inspectors are most accustomed to. And is anything I'm proposing below not actually code-compliant?
Scenario 1:
customer-owned transformer 2000kVA, 15kV delta:480V wye, pad mounted outside, 3000A disconnect on same pad.
Scenario 2:
Exactly the same as Scenario 1, except now its a service transformer. 3000A disco is now service disco and still outside on the same pad and xfmr. Does anything change?
I think most transformers do not come with a ground space large enough for 8 sets of SSBJ may be a problem, unless we're savvy when ordering the transformer (which can easily be missed)
Scenario 1:
customer-owned transformer 2000kVA, 15kV delta:480V wye, pad mounted outside, 3000A disconnect on same pad.
- Option1A: ground Xo bushing, do not bond N-G in switchboard. Run 8 PVC conduits with phase, N, and SSBJ in each conduit.
- Option1B: ground Xo bushing, do not bond N-G in switchboard. Run 8 PVC conduits with phase and N only. Run one large SSBJ buried in the pad from Xo to switchboard G bus.
- Option 1C: do not ground Xo bushing, bond N-G in switchboard. Run 8 PVC conduits with phase, N, and SSBJ in each conduit.
- Option 1C: do not ground Xo bushing, bond N-G in switchboard. Run 8 PVC conduits with phase and N in each conduit. Run one large SSBJ buried in the pad from Xo to switchboard G bus.
Scenario 2:
Exactly the same as Scenario 1, except now its a service transformer. 3000A disco is now service disco and still outside on the same pad and xfmr. Does anything change?
I think most transformers do not come with a ground space large enough for 8 sets of SSBJ may be a problem, unless we're savvy when ordering the transformer (which can easily be missed)