Generator Grounding

Status
Not open for further replies.

DMG_1

Member
Location
Boston, MA, USA
I have a question regarding generator grounding. Many times I have seen a ground ring with ground rods put around a generator. If the generator is NOT a separately derived system, does the ground ring and ground rods simply get connected to the equipment grounding conductor? This leads to another question, in this example, is the ground ring required.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
With a non-SDS the neutral is isolated and there is generally no requirement for a connection to a GES. However, the manufacturer or designer may require some type of grounding electrode that is connected to the generator frame which is ultimately connected to the EGC with the feeder.
 

Dale001289

Senior Member
Location
Georgia
I have a question regarding generator grounding. Many times I have seen a ground ring with ground rods put around a generator. If the generator is NOT a separately derived system, does the ground ring and ground rods simply get connected to the equipment grounding conductor? This leads to another question, in this example, is the ground ring required.

Installation of a ground ring is more of a common practice than a requirement - even for non-SDS generators. You’d still want to bond to the generator frame - as a minimum.


Sent from my iPhone using Tapatalk
 

david

Senior Member
Location
Pennsylvania
With a non-SDS the neutral is isolated and there is generally no requirement for a connection to a GES. However, the manufacturer or designer may require some type of grounding electrode that is connected to the generator frame which is ultimately connected to the EGC with the feeder.

250.30 (C ) 2011, 2014

im under 2008 but i think either 2011 or 2014 changed the requirement for outside transformers to all outside SDS, though in this case it is not an SDS
 

publicgood

Senior Member
Location
WI, USA
With a non-SDS the neutral is isolated and there is generally no requirement for a connection to a GES. However, the manufacturer or designer may require some type of grounding electrode that is connected to the generator frame which is ultimately connected to the EGC with the feeder.

Agree
 