Isolated Ground Outside of Raceway

Status
Not open for further replies.

KWH

Senior Member
A isolated ground is considered an egc, so when installed with feeders to panel it would have to be inside the conduit correct or is there an exception besides 6ft rule where it could be ran like a gec.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Would this apply?

254.146(D) Isolated Ground Receptacles. Where installed for the
reduction of electrical noise (electromagnetic interference)
on the grounding circuit, a receptacle in which the ground-
ing terminal is purposely insulated from the receptacle
mounting means shall be permitted. The receptacle ground-
ing terminal shall be connected to an insulated equipment
grounding conductor run with the circuit conductors
. This
equipment grounding conductor shall be permitted to pass
through one or more panelboards without a connection to
the panelboard grounding terminal bar as permitted in
408.40, Exception, so as to terminate within the same
building or structure directly at an equipment grounding
conductor terminal of the applicable derived system or ser-
vice. Where installed in accordance with the provisions of
this section, this equipment grounding conductor shall also
be permitted to pass through boxes, wireways, or other
enclosures without being connected to such enclosures.
 

DrSparks

The Everlasting Know-it-all!
Location
Madison, WI, USA
Occupation
Master Electrician and General Contractor
Isolated Ground Outside of Raceway

A isolated ground is considered an egc, so when installed with feeders to panel it would have to be inside the conduit correct or is there an exception besides 6ft rule where it could be ran like a gec.

No it would create a high impedance ground not being run with the circuit conductors. Even of CODE allowed it, from an engineering standpoint it would be asinine.


Sent from my iPhone using Tapatalk
 

tom baker

First Chief Moderator
Staff member
the code focuses on the how, not the why. There is a hint in 300.5
When all the circuit conductors are in close proximity (IE inside the raceway) the magnetic fields cancel and in a ground fault, with a EGC, have a low impedance. If the egc is on the outside, over 6 ft, the impedance is so high the OCPD may not open.
 