    Are the push on grounding clips that can be used for box bonding as required by 250.148(C) listed items?
    If so, does anyone know what UL category covers them?
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)

    #2
    These NSI clips have a UL stamp on them.

    Roger
    Moderator

    Comment


      #3
      Originally posted by don_resqcapt19 View Post
      Are the push on grounding clips that can be used for box bonding as required by 250.148(C) listed items?
      If so, does anyone know what UL category covers them?
      They are covered under UL category KDER.

      Comment


        #4
        Originally posted by packersparky View Post
        They are covered under UL category KDER.
        I thought they would be but when I look up Raco's part number for that clip, it does not show up in the list of part number that they have listed in the category.
        Don, Illinois
        (All code citations are 2017 unless otherwise noted)

        Comment


          #5
          Originally posted by roger View Post
          These NSI clips have a UL stamp on them.

          Roger
          Thanks. However they can't be used in the field as they are UL Recognized and not UL listed.
          http://www.nsiindustries.com/UserFil...rounding17.pdf
          Don, Illinois
          (All code citations are 2017 unless otherwise noted)

          Comment


            #6
            Originally posted by don_resqcapt19 View Post
            Thanks. However they can't be used in the field as they are UL Recognized and not UL listed.
            http://www.nsiindustries.com/UserFil...rounding17.pdf
            I note they carry the “Listed” rather than “Recognized” UL mark on the clip itself.
            "Bob"
            Robert B. Alexander, P.E.
            Answers based on 2017 NEC unless otherwise noted.

            Comment


              #7
              Originally posted by rbalex View Post
              I note they carry the “Listed” rather than “Recognized” UL mark on the clip itself.
              It may be both listed and recognized.
              Bob

              Comment


                #8
                Originally posted by petersonra View Post
                It may be both listed and recognized.
                It does not appear on the list of their products that are listed under that category.
                Don, Illinois
                (All code citations are 2017 unless otherwise noted)

                Comment


                  #9
                  Originally posted by rbalex View Post
                  I note they carry the “Listed” rather than “Recognized” UL mark on the clip itself.
                  That is interesting as that part number is not on the list of UL listed parts under KDER.
                  Don, Illinois
                  (All code citations are 2017 unless otherwise noted)

                  Comment


                    #10
                    Originally posted by don_resqcapt19 View Post
                    That is interesting as that part number is not on the list of UL listed parts under KDER.
                    why don't you ask them?

                    My guess is that it would be covered under option 7 in 250.8

                    250.8 Connection of Grounding and Bonding Equipment.
                    (A) Permitted Methods. Equipment grounding conductors,
                    grounding electrode conductors, and bonding jumpers shall be
                    connected by one or more of the following means:
                    (1) Listed pressure connectors
                    (2) Terminal bars
                    (3) Pressure connectors listed as grounding and bonding
                    equipment
                    (4) Exothermic welding process
                    (5) Machine screw-type fasteners that engage not less than
                    two threads or are secured with a nut
                    (6) Thread-forming machine screws that engage not less than
                    two threads in the enclosure
                    (7) Connections that are part of a listed assembly
                    (8) Other listed means
                    Listed assemblies can include assemblies that are field assembled. In any case, the code does not require ground screws to be listed, or terminal bars for that matter.
                    Bob

                    Comment


                      #11
                      [QUOTE=petersonra;1975648]why don't you ask them?

                      My guess is that it would be covered under option 7 in 250.8



                      Listed assemblies can include assemblies that are field assembled. In any case, the code does not require ground screws to be listed, or terminal bars for that matter.[/QUOTE]

                      There is no way that I will ever see a field installed ground clip as being part of a listed assembly. It is my opinion that a the grounding clips are covered under list item 8 in 250.8.
                      The following is from UL.

                      Because components are only intended for installation in end products whose safety is evaluated by UL separately, they may be incomplete in construction or restricted in

                      performance capabilities. This factor precludes their safe installation by electricians or contractors in the field.