    how to size GEC for 800 amp service

    I have a 800 amp 3 phase service being fed with parallel 500 mcm copper conductors.

    Table 250.66 gives me the sizing for the GEC. Do I just double the 500 mcm by 2 and call it 1000mcm which would fall under the 2/0 CU?
    I'm an electrician not a magician !

    #2
    correct
    (with exceptions for ground rods and concrete-encased electrodes)
    Last edited by augie47; 02-01-19, 11:02 AM.