Any potential violatIons on taking an GEC (coming from bldg steel for example) through a Single lug on XO and loop it thru and hit xfmr enclosure to also serve as the system bonding jumper? Say it’s a 75kva 480v to 208v xfmr typical setup, with bonding done inside xfmr. Looking thru 250.24 I don’t see that it would be. Correct me if I’m wrong


Sent from my iPhone using Tapatalk
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Any potential violatIons on taking an GEC (coming from bldg steel for example) through a Single lug on XO and loop it thru and hit xfmr enclosure to also serve as the system bonding jumper? Say it’s a 75kva 480v to 208v xfmr typical setup, with bonding done inside xfmr. Looking thru 250.24 I don’t see that it would be. Correct me if I’m wrong


Sent from my iPhone using Tapatalk

I see nothing wrong with it.
 