Grounding to Rod

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
Curious of a few things. Inside a building with slab already poured

Can EMT be used from panel to ground rod or is it code to use RGS?
Would obviously have to penetrate slab to sink ground rod?
Would 1/2" conduit run right to ground row with no exposed wiring showing?


Never came across this scenario.
 

Attachments

  • Capture.jpg
    Capture.jpg
    14.1 KB · Views: 0
  • Capture 2.jpg
    Capture 2.jpg
    13.3 KB · Views: 0

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Technically no raceway is required if not subject to physical damage but we always use EMT for aesthetic reasons. Imagine what this would look like of all of the GEC's were run free air.

20180815_091915.jpg
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Just don't forget that you have to bond the GEC to the EMT at both ends unless you are using aluminum EMT.
 