    Grounding to Rod

    Curious of a few things. Inside a building with slab already poured

    Can EMT be used from panel to ground rod or is it code to use RGS?
    Would obviously have to penetrate slab to sink ground rod?
    Would 1/2" conduit run right to ground row with no exposed wiring showing?


    Never came across this scenario.
    Attached Files

    #2
    Technically no raceway is required if not subject to physical damage but we always use EMT for aesthetic reasons. Imagine what this would look like of all of the GEC's were run free air.

    Click image for larger version

Name:	20180815_091915.jpg
Views:	2
Size:	148.3 KB
ID:	2380670
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

    Comment


      #3
      Just don't forget that you have to bond the GEC to the EMT at both ends unless you are using aluminum EMT.
      Don, Illinois
      (All code citations are 2017 unless otherwise noted)

      Comment


        #4
        Originally posted by infinity View Post
        Technically no raceway is required if not subject to physical damage but we always use EMT for aesthetic reasons. Imagine what this would look like of all of the GEC's were run free air.

        [ATTACH=CONFIG]22760[/ATTACH]
        Rob, are those all for SDS's or something else?
        Ethan Brush - East West Electric. NY, WA. MA

        "You can't generalize"

        Comment


          #5
          Originally posted by electrofelon View Post
          Rob, are those all for SDS's or something else?
          Yes, a combination of 4-4000 amp services, common grounding risers, and multiple step up transformers within the service room.
          Rob

          Moderator

          All responses based on the 2014 NEC unless otherwise noted

          Comment


            #6
            Originally posted by infinity View Post
            Yes, a combination of 4-4000 amp services, common grounding risers, and multiple step up transformers within the service room.
            Cool. Very pretty.
            Ethan Brush - East West Electric. NY, WA. MA

            "You can't generalize"

            Comment


              #7
              Originally posted by infinity View Post
              [ATTACH=CONFIG]22760[/ATTACH]
              Why does this picture make me think of a church?
              Master Electrician
              Electrical Contractor
              Richmond, VA

              Comment


                #8
                Originally posted by LarryFine View Post
                Why does this picture make me think of a church?
                Needs some stained glass to go with it.
                I live for today, I'm just a day behind.

                Comment


                  #9
                  Originally posted by infinity View Post
                  Technically no raceway is required if not subject to physical damage but we always use EMT for aesthetic reasons. Imagine what this would look like of all of the GEC's were run free air.

                  [ATTACH=CONFIG]22760[/ATTACH]
                  They are going to be in free air for the last foot or so.
                  I live for today, I'm just a day behind.

                  Comment


                    #10
                    Originally posted by electrofelon View Post
                    Cool. Very pretty.
                    Thanks.
                    Rob

                    Moderator

                    All responses based on the 2014 NEC unless otherwise noted

                    Comment


                      #11
                      Originally posted by LarryFine View Post
                      Why does this picture make me think of a church?
                      Usually a pipe organ has pipes of different lengths.

                      Comment