MRKN
Member
- Location
- California, USA
I cannot find any requirement in the NEC for a grounding electrode at every piece of electrical equipment such as at a motor.
Yes, at every building or structure served per 250.32.
But in fact, it seems that it is specifically prohibited under 250.30(A):
(A) Grounded Systems. A separately derived ac system that is
grounded shall comply with 250.30(A)(1) through (A)(8).
Except as otherwise permitted in this article, a grounded
conductor shall not be connected to normally non–current carrying
metal parts of equipment, be connected to equipment
grounding conductors, or be reconnected to ground on the
load side of the system bonding jumper.
Informational Note: See 250.32 for connections at separate
buildings or structures and 250.142 for use of the grounded
circuit conductor for grounding equipment.
250.142(B) gives a few exceptions to this, but more importantly the handbook has two explanatory paragraphs as to why following this section. In the case of a 3-ph motor with no neutral wire it's not clear that their example is applicable as to the logic.
Yes, at every building or structure served per 250.32.
But in fact, it seems that it is specifically prohibited under 250.30(A):
(A) Grounded Systems. A separately derived ac system that is
grounded shall comply with 250.30(A)(1) through (A)(8).
Except as otherwise permitted in this article, a grounded
conductor shall not be connected to normally non–current carrying
metal parts of equipment, be connected to equipment
grounding conductors, or be reconnected to ground on the
load side of the system bonding jumper.
Informational Note: See 250.32 for connections at separate
buildings or structures and 250.142 for use of the grounded
circuit conductor for grounding equipment.
250.142(B) gives a few exceptions to this, but more importantly the handbook has two explanatory paragraphs as to why following this section. In the case of a 3-ph motor with no neutral wire it's not clear that their example is applicable as to the logic.