xguard
Senior Member
- Location
- Baton Rouge, LA
We have a building with two service disconnects side by side. They are each fed from the same utility transformer but with separate runs. Both runs pass through the same current transformer box and share a meter.
Where I'm confused is in sizing the common portions of grounding electrode conductors. I'm wondering if there is a difference between this and a single run tapped off to two disconnects.
If each disconnect is supplied by it's own set of parallel (two per phase) 500 kcmil then the common grounding electrode conductors should be 3/0 and the taps off this 3/0 to each disconnect should be 2/0?
What about supply side bonding jumpers in a wire-way shared by both, on the line side of the disconnects?
Let me know if this isn't clear, I'm struggling some describing it.