    Two family with house meter bond and grounding question.

    Hi
    I am working on a two family house with three gang meter sockets. three 100 amp main breaker panels .
    I am replacing one panel so have to upgrade grounding. my question is where does water main ground go? To the first panel neutral bar? and ground rod to all panels in and out from neutral to neutral and does it have to be continuous unbroken. from panel to panel. what are my options? Thank you in advance

    #2
    Originally posted by digitaltwist View Post
    Hi
    I am working on a two family house with three gang meter sockets. three 100 amp main breaker panels .
    Three meter sockets in one common enclosure? Where is the service disconnect in relation to the main breaker panels?

    I am replacing one panel so have to upgrade grounding. my question is where does water main ground go? To the first panel neutral bar? and ground rod to all panels in and out from neutral to neutral and does it have to be continuous unbroken. from panel to panel. what are my options? Thank you in advance
    Upgrade why? What is there now?
    If Billy Idol is on your playlist go reevaluate your life.

    Comment


      #3
      YES Three meter sockets in one common enclosure.
      NO service disconnect. Each panel is feed from the meter enclosure and all three panel have 100 amp main breakers.

      Comment


        #4
        The code applied here is nyc code.

        Comment


          #5
          Originally posted by digitaltwist View Post
          Hi
          I am working on a two family house with three gang meter sockets. three 100 amp main breaker panels .
          I am replacing one panel so have to upgrade grounding. my question is where does water main ground go? To the first panel neutral bar? and ground rod to all panels in and out from neutral to neutral and does it have to be continuous unbroken. from panel to panel. what are my options? Thank you in advance
          See 250.64(D). That gives you the options for the earthing connections for multiple service disconnect enclosures. I generally find the "common location" method made in the meter to be the easiest for multi gang sockets without disconnects
          Ethan Brush - East West Electric. NY, WA. MA

          "You can't generalize"

          Comment


            #6
            meter socket grounding work for me in this case.
            any other suggestions?

            Comment


              #7
              Originally posted by digitaltwist View Post
              meter socket grounding work for me in this case.
              any other suggestions?
              I don't have any further suggestions. Do you have a specific question?
              Ethan Brush - East West Electric. NY, WA. MA

              "You can't generalize"