Communication Manhole Cover bonding

Status
Not open for further replies.

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Anyone knows any reference if bonding of communication manhole covers are required by the code? Thank you

Presumably you are asking about the National Electrical Code. If so, it would appear the answer depends on whether or not the manhole is under the exclusive control of the communications utility.

90.2 Scope.
(B) Not Covered. This Code does not cover the following:
***
(4) Installations of communications equipment under the
exclusive control of communications utilities located
outdoors or in building spaces used exclusively for such
installations
 