Maximum size of System Bonding Jumper in Transformer Derived System

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Need to confirm maximum size system bonding jumper in a transformer with (12) sets of (4) 750 MCM CU feeders on the secondary side?

There is no maximum size but there is a minimum. You would take size of the ungrounded conductor times the number of sets and then multiply by 12.5%.

12*750 kcmil=9000 kcmil*12.5%=1125 kcmil
 

kwired

Electron manager
Location
NE Nebraska
Trying to wrap my head around 12 sets of 4, or did you mean 4 sets of 12?

Three phase four wire can have 4 sets of 12.

12 sets of four= 12 phase system??
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
There is no maximum size but there is a minimum. You would take size of the ungrounded conductor times the number of sets and then multiply by 12.5%.

12*750 kcmil=9000 kcmil*12.5%=1125 kcmil

:thumbsup:
 

kwired

Electron manager
Location
NE Nebraska
12 sets of 4 conductors in each set. A,B,C,N
so 12 elements in parallel and 4 effective conductors.

Guess that is what I was thinking, but for some reason it just didn't sound right.

12 x 750 kcmil, just a little bit of current that can flow here.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
so 12 elements in parallel and 4 effective conductors.

Guess that is what I was thinking, but for some reason it just didn't sound right.

12 x 750 kcmil, just a little bit of current that can flow here.

Yes so in this case (unless there is some adjustment factor) you end up with a 5700 amp set of secondary conductors.
 

Todd Smith

Member
Location
Charleston, SC
Yes - 12 sets of 750 MCM Cu A,B,C,N - 12 sets in parallel

Yes - 12 sets of 750 MCM Cu A,B,C,N - 12 sets in parallel

Reply - Wasn't there a past code that indicated 3/0 was the maximum?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Reply - Wasn't there a past code that indicated 3/0 was the maximum?

No, although the table 250.102(C) is relatively new the old section 250.28(D) had the same requirements for 12.5% in the 2005 NEC. #3/0 is still the largest required GEC.
 