Announcement
Collapse
No announcement yet.
Swimming pool bonding on vinyl support posts??
Collapse
X
  • Filter
  • Time
  • Show
Clear All
new posts
    I have an above ground swimmimg pool that I need to bond but upon starting this job I discovered that the support posts on the pool are not metal at all but actually plastic. I can bond the pump, the outlet, the pool water, and the earth around it but the posts themselves have no metal to speak of. However the liner bead, post top mounts and wall bottom rails are steel. With plastic posts how do I bond the top and bottom pool steel together?? Has anyone else encountered a pool install like this??
    #2
    I haven't encountered an above ground pool like this but have a similar experience with in ground concrete pools. On the top of the concrete wall is where the liner hanger was mounted. It consisted of several metal sections that went around the top of the wall. Coping stone was to be put on top of these metal hangers. The inspectors had me put a lug in each section (16 I think) and run a #8 around the top, through each of the lugs.
    Since I also had the perimeter bond loop at the bottom, I had to run a jumper from the top loop to the bottom using split bolts.
    You may have to do something similar with the AG pool. If there is a way to hide the loop at the top, you could run it, then another at the bottom and jump them together. Of course if the metal you speak of is not continuous, you would have to add lugs to each section and do as I did on the IG pool.
    [COLOR=navy]If you aim at nothing, you will hit it every time![/COLOR]
    Comment
      #3
      I can probably conceal the bonding wires from the top cap to the bottom post mount inside the posts themselves. I think I will have to actually remove one post at a time from the pool wall in order to access the bottom mounting plate and add a lay in lug for the wire. and run it inside each post to the top cap, but I do believe it can be done. Thank you for very much for your advice. Have a blessed evening. [emoji846]
      Sent from my SM-G955U using Tapatalk
      Comment
        #4
        Everything seems to be plastic except this metal skin (not the vertical dark colored parts he seems to be pointing at)
        How do y'all usually attach to it?
        Think for yourself, while its still somewhat legal!
        Clarkesville, Georgia
        Comment
          #5
          Some pool companies make a fitting that attaches to the metal support however you could drill it and install a lug or your wire.
          They say I shot a man named Gray and took his wife to Italy
          She inherited a million bucks and when she died it came to me
          I can't help it if I'm lucky
          Comment
            #6
            Thanks!
            But the supports are not metal, it's the sheeting that is. The stuff with the wavy lines
            Comment
              #7
              We don't deal with any above ground pools-wish I could help you out.
              I would call the pool kit manufacturer and ask them. They must have insights on how their dealers bond their structures. I'll bet it's a common question for them.
              What I do know, is that the metal wall is joined together at some point with numerous screws/bolts. I would think at this point a bond lug would be attached. If the top cap is metal, it's probably in sections which means the bond wire will have to jump to each section much like metal fence posts that have removable sections between them.
              Comment
                #8
                I have never dealt with a pool exactly like the OP. But I have dealt with metal sided pools that are classified as either underground or partially underground. What they have is metal sections that bolt together. I removed one of the bolts and placed a lay-in lug over the hole, then put the bolt back through (if it was long enough) along with the nut. Since these sections are made "mechanically continuous" I just hit the four points, equally spaced, around the pool.
                If the pool in the OP is not continuous then each section would have to be made continuous by either a continuous loop through each lug or bonding jumpers between them.
                Comment
                  #9
                  2 great answers, thanks to both!
                  Comment
                    #10
                    The metal is plastic coated, does that change situation?
                    Comment
                      #11
                      Not too much. It just means you must bond those support posts.
                      Comment
                        #12
                        Thanks!
                        thank god for inground pools. now all i have to figure out is where this sand goes.
                        fortunately, it doesn't require bonding.
                        Click image for larger version
                        ~New signature under construction.~
                        ~~~~Please excuse the mess.~~~~
                        Comment
                          #13
                          [ATTACH=CONFIG]23405[/ATTACH]
                          Couple of palm trees, lounge chair, and a drink with a tiny umbrella and your set. You'll be the envy of your neighbors
                          Just no tacky Hawaiian shirts
                          Comment
                            #14
                            this was after today. my friend danny who is helping with this, did this by
                            himself, in 6 hours. 12 tons in 6 hours, wheeled 100', and spread with a rake.
                            it was raining when we started at 6:30am, and hot and humid after that.
                            danny? oh, his birthday was last month. he turned 64. i had to go do some
                            work, and left him unsupervised.
                            Comment
                            Working...
                            X