    250.50

    Click image for larger version

Name:	ss.jpg
Views:	1
Size:	16.9 KB
ID:	2388982
    Per this exhibit, all electrodes shall be bonded together, my question is "where the bonding will be, in building or in ground?"

    For communication, i think bonding shall be in building but i am not sure for other electrodes like steel rebars & water pipes.
    "Sleem"

    #2
    I'm not sure I understand the question. You can jumper from one electrode to another, and if that path takes you underground so be it.
    If Billy Idol is on your playlist go reevaluate your life.

    Comment


      #3
      I believe 250.68(A) addresses that in "accessibility"
      At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

      Comment


        #4
        Originally posted by augie47 View Post
        I believe 250.68(A) addresses that in "accessibility"
        It could be accessible in ground through inspection pit.
        "Sleem"

        Comment


          #5
          Originally posted by ActionDave View Post
          I'm not sure I understand the question. You can jumper from one electrode to another, and if that path takes you underground so be it.
          I am referring to the exhibit which shows different electrodes bonded together above ground, I am just confirming that it's not mandatory to bond above ground.
          "Sleem"

          Comment


            #6
            Originally posted by m sleem View Post
            I am referring to the exhibit which shows different electrodes bonded together above ground, I am just confirming that it's not mandatory to bond above ground.
            It is not necessary to bond above ground, and you don't need a lot.
            If Billy Idol is on your playlist go reevaluate your life.

            Comment


              #7
              Originally posted by m sleem View Post
              I am referring to the exhibit which shows different electrodes bonded together above ground, I am just confirming that it's not mandatory to bond above ground.
              Can depend on bonding method, but as general rule not necessary to be above ground. Connection doesn't need to be accessible for buried electrodes, say a jumper from one ground rod to another or from a CEE to another electrode, must of course use a connection method rated for the conditions.

              Bonds to building steel or to a water pipe electrode must remain accessible though. A CEE that is extended out of the concrete to make connection must also have accessibility to that connection, but if the connection is encased in the concrete that is fine as long as it is a connection rated to be encased in concrete.
              I live for today, I'm just a day behind.