    Beyond substations with exposed/energized equipment/busses, (and maybe swimming pools) is there any other condition where the NEC requires fencing to be grounded? Just reviewed a plan for perimeter fencing around a large gas facility, which specs grounding of fence posts. I'm not sure of the basis or technical justification for this.

    #2
    Originally posted by nhee2 View Post
    Beyond substations with exposed/energized equipment/busses, (and maybe swimming pools) is there any other condition where the NEC requires fencing to be grounded? Just reviewed a plan for perimeter fencing around a large gas facility, which specs grounding of fence posts. I'm not sure of the basis or technical justification for this.
    Often, the basis and justification for doing something is that "we have always done it that way".

    AFAIAC, you can't get much better grounded that a metal pole stuck in some concrete in the ground.
    Bob

    Comment


      #3
      Originally posted by nhee2 View Post
      Beyond substations with exposed/energized equipment/busses, (and maybe swimming pools) is there any other condition where the NEC requires fencing to be grounded? Just reviewed a plan for perimeter fencing around a large gas facility, which specs grounding of fence posts. I'm not sure of the basis or technical justification for this.
      To limit sparking as an ignition source would be a SEWAG.
      Tom
      TBLO

      Comment


        #4
        Originally posted by ptonsparky View Post
        To limit sparking as an ignition source would be a SEWAG.
        I don't know what would be the initiator of the spark, if there are no electrical sources in the vicinity. and if they are just grounding every few posts (not every post) then it seems to not provide any value.

        Comment


          #5
          IDK either, but it puts everything at the same potential.
          Tom
          TBLO

          Comment


            #6
            Originally posted by petersonra View Post
            Often, the basis and justification for doing something is that "we have always done it that way".

            AFAIAC, you can't get much better grounded that a metal pole stuck in some concrete in the ground.
            Did a 2 MW solar farm two years ago. Had whatever it was - almost a mile perimeter of fencing. Metal posts in concrete. We had to drive a ground rod every 200 feet to "ground" the fence
            Ethan Brush - East West Electric. NY, WA. MA

            "You can't generalize"

            Comment


              #7
              This is usually IEEE driven. In a substation environment IEEE 80 states that fencing should be bonded and grounded and makes a big deal about the fence. There are also vague questions about how far the equipment should be from a fence. And the whole ground grid thing is crazy once you get away from overhead tubular construction. Might be due to induced voltages. In testing around 230 kV subs once in a while and by this I mean 2-3% of the time I will find maybe one rod that has a high resistance and they’re all bonded together but this is rare.

              So might want to start with that standard. IEEE standards are a little annoying because often they are more of a cookbook with little or no guidance and it’s up to the end user to find the right recipe. There were even 2 partial sentences in the IEEE arc flash standard (1584-2002) where a couple things were mentioned more or less in passing like the 2 second rule. They became almost enshrined as requirements.


              Sent from my iPhone using Tapatalk

              Comment


                #8
                Originally posted by paulengr View Post
                This is usually IEEE driven. In a substation environment IEEE 80 states that fencing should be bonded and grounded and makes a big deal about the fence. There are also vague questions about how far the equipment should be from a fence. And the whole ground grid thing is crazy once you get away from overhead tubular construction. Might be due to induced voltages. In testing around 230 kV subs once in a while and by this I mean 2-3% of the time I will find maybe one rod that has a high resistance and they’re all bonded together but this is rare.

                So might want to start with that standard. IEEE standards are a little annoying because often they are more of a cookbook with little or no guidance and it’s up to the end user to find the right recipe. There were even 2 partial sentences in the IEEE arc flash standard (1584-2002) where a couple things were mentioned more or less in passing like the 2 second rule. They became almost enshrined as requirements.
                Thanks for the response. I agree IEEE 80 would provide guidance for substations and grounding of fence in a substation. I am guessing the details shown in the drawings I reviewed are a cut-and-paste from a substation job. in this case I don't think IEEE 80 applies. They'll be installing 5000 ft of 4/0 copper, a bunch of rods, clamps, cad-welds, etc. with (in my opinion) very little if any benefit. There's some MV distribution on site that comes in below-grade to a switchgear lineup, but no overhead distribution or other installation that could be considered substation.