as per 250.52 B all it needs is to be "effectively bonded." no specific description on the code so related sections will govern : code sized GEC, code approved connections, physically secured from damage, less than 25ohms resistance (test point at the busbar)
Assuming the above are met then the installation is valid, have a written explanation concurred by a PE to satisfy the Inspector.
But If I were the inspector I will pass it only if certified by a PE.
Interconnecting the GE's is a method of lowering the resistance, minimizing potential difference between GEs and effectively distributing the dissipation of fault current. Tried & tested. NEC is only a minimum requirement. it is not always the most efficient best practice.
My interest is that, are wiring Permits issued without an electrical plan signed and sealed by a PE ? why are contractors allowed to decide on this, its the designers job to provide the details for this, if field details are proposed then Designers recommending approval is needed, this would not happen if the contractor employs the service of a PE for its projects.
Is this the prevailing practice on this area?
If I were the client, regardless of contract,I will nail the contractor for not giving the best practice available, whats the cost of interconnecting wire and clamps and the digging ? peanuts! theres always excess phase wires for every job. its not worth the delay in energization.