It's been a while since I've submitted in this forum first question what is a CCE or CEE?
Second question. Specification on a project requires 5ohm resistance or less for the grounding systems. Testing used was the fall of potential method at 62%. Three rods were installed initially. The ground resistance was 50.5ohms. The contractor installed 2 more rods and resistance went to 50ohms. We found out that the installation is at the top of a berm. (really rocky with dirt mixed in to fill the gaps). We went to the bottom of the berm approximately 50 to 75 feet away from the service, and installed a rod, the reading went to 36ohms. We pounded 3 additional rods and fiinal got a reading of 23.6ohms which meets the minimal requirment of the NEC. I contacted the AHJ for permission to walk away at this point which he agreed.
So the question is when should you walk away from something like this? The site is very small and there was no rebar installed so a UFER ground was not available. The soil in the area is really rocky and several of the rods could not be driven deep enough to meet the 8' requirements of the code.
A seasoned veteran in my office sugested that the NEC requires you to install one ground rod for your system. When measured, if the resistance is greater than 25ohms then all you need to do is install one supplemental rod and then walk away. Is this the correct interpertation?
Second question. Specification on a project requires 5ohm resistance or less for the grounding systems. Testing used was the fall of potential method at 62%. Three rods were installed initially. The ground resistance was 50.5ohms. The contractor installed 2 more rods and resistance went to 50ohms. We found out that the installation is at the top of a berm. (really rocky with dirt mixed in to fill the gaps). We went to the bottom of the berm approximately 50 to 75 feet away from the service, and installed a rod, the reading went to 36ohms. We pounded 3 additional rods and fiinal got a reading of 23.6ohms which meets the minimal requirment of the NEC. I contacted the AHJ for permission to walk away at this point which he agreed.
So the question is when should you walk away from something like this? The site is very small and there was no rebar installed so a UFER ground was not available. The soil in the area is really rocky and several of the rods could not be driven deep enough to meet the 8' requirements of the code.
A seasoned veteran in my office sugested that the NEC requires you to install one ground rod for your system. When measured, if the resistance is greater than 25ohms then all you need to do is install one supplemental rod and then walk away. Is this the correct interpertation?