    liquid tight flexible conduit bonding

    In Class I Division 2 location when connecting motors with LFMC where an equipment ground conductor is contained within the LFMC, I believe an external bonding jumper is not require since the internal ground conductor serves the bonding purpose. True?

    #2
    I believe you are correct as far as the NEC is concerned.