    Ground wire

    Sub panel without a ground wire

    #2
    Need more info and what is your question?

    Roger
    Moderator

    Comment


      #3
      Originally posted by gibgin View Post
      Sub panel without a ground wire
      Are you suggesting it does not have a grounding electrode conductor? Or an equipment grounding conductor? Or a grounded conductor?

      If it is a panel fed from another panel it generally does not require a grounding electrode conductor (unless in a separate structure).

      If it uses metallic conduit or EMT the EMT or conduit can serve as the equipment grounding conductor.

      If there are no L-N loads no grounded conductor is actually required.
      Bob

      Comment


        #4
        Originally posted by roger View Post
        Need more info and what is your question?

        Roger
        I agree, sub-panel pre-2008 and separate structure no EGC required.
        Rob

        Moderator

        All responses based on the 2017 NEC unless otherwise noted