I recently installed a 200 amp service on a pole for a mobile home. I used a separate meter base & 200 amp panel with a 2inch nipple In between. My question is will the Square D B200 hub satisfy 250.92? The concentric knockout in the bottom of the meterbase goes to 2.5".
Announcement
Collapse
No announcement yet.
Service entrance bonding.
Collapse
X
-
Yes, as Larry mentioned. Just remember that if your meter can is not permanently factory bonded it would have come with a jumper to field install in this case.
I only mention this as these days more and more meter sockets are coming with a removable main bonding jumper.
Comment
-
Originally posted by texie View PostYes, as Larry mentioned. Just remember that if your meter can is not permanently factory bonded it would have come with a jumper to field install in this case.
I only mention this as these days more and more meter sockets are coming with a removable main bonding jumper.Master Electrician
Electrical Contractor
Richmond, VA
Comment
-
Originally posted by LarryFine View Post
I've never seen a never base that did not have the neutral bus/terminal block bolted directly to the enclosure.
Comment
-
Originally posted by nickelec View PostIn some buildings in the city the meters are located on the floor of the customer served in these situations we need to buy an isolation kit to isolate the neutral from the enclosure
Sent from my SM-G965U using TapatalkI live for today, I'm just a day behind.