    I have always thought that the horizontal rebar used as a concrete encased electrode had to be "near the bottom" of the footing or foundation. Now it has brought to my attention that the "near the bottom" part went away in the 2011 NEC. I haven't had a chance yet to go dig for the substantiation. Does anyone know why they removed the wording? And would tying on to rebar in the top of a foundation wall really suffice?

    #2
    Does it still say 'in the footing?" That would eliminate the foundation wall as an option. Can it be in the floor slab? I know it has to be un-coated, bare iron.

    Comment


      #3
      My guess is that there is no definition of "near the bottom" and in fact it doesn't matter where it is in the footing as long as it's encased in concrete.
      Rob

      Moderator

      All responses based on the 2017 NEC unless otherwise noted

      Comment


        #4
        250.52(a)(3) - ..."and shall be located horizontally within that portion of a concrete foundation or footing that is in direct contact with the earth..."
        It doesn't seem to specify in the footing but just gives it as an option. I'm thinking you could argue that any 20'+ section of rebar in the wall could be used as long as the wall touches dirt.

        Comment


          #5
          Originally posted by jdiv View Post
          250.52(a)(3) - ..."and shall be located horizontally within that portion of a concrete foundation or footing that is in direct contact with the earth..."
          It doesn't seem to specify in the footing but just gives it as an option. I'm thinking you could argue that any 20'+ section of rebar in the wall could be used as long as the wall touches dirt.
          ...and is not coated with any insulating material. Foundatioin walls with occupied spaces inside often have waterproofing coatings applied to the exterior side, which will inhibit effectiveness of any CEE that may be contained.
          I live for today, I'm just a day behind.

          Comment


            #6
            Originally posted by jdiv View Post
            250.52(a)(3) - ..."and shall be located horizontally within that portion of a concrete foundation or footing that is in direct contact with the earth..."
            It doesn't seem to specify in the footing but just gives it as an option. I'm thinking you could argue that any 20'+ section of rebar in the wall could be used as long as the wall touches dirt.
            Shall be located is not an option. It needs to be in a footer or foundation and the grounding electrode conductor must be connected in that portion of a footing or foundation that is in direct contact with the earth
            They say I shot a man named Gray and took his wife to Italy
            She inherited a million bucks and when she died it came to me
            I can't help it if I'm lucky

            Comment


              #7
              Thank you for your answers.