Hi Guy's,
I recently purchased a 1950's property where the previous owner replaced the old panel with a new one which has an isolated neutral bar and a ground bar and an egc to ground rod. The feeder for this panel is three wire and originates from a fused 100 amp disconnect which is downstream of the meter and is the main service disconnect. The neutral wire from the meter to the service disconnect is bonded to ground in the chaise above the meter via a lug connector. Should the main panel neutral and ground bars be bonded or should they be isolated? I have read a bunch of posts on the subject and they seem to suggest that: After 2008 nec code requires an egc from the main service disconnect (fused 100 amp disconnect in this case) to the panel (4 wire), and the panel should be grounded via ground rod with isolated neutral and ground bars inside the panel.
Prior to 2008 code would allow the panel to be connected via the 3 wire feeder back to the main disconnect, without separate egc, and with bonded neutral and ground bars
I'd like to know what the preferred way to update this setup would be? I don't know exactly when the panel was installed but I'd guess after 2008. My concern here is having an electrical system that conforms to code at the time it was installed. Thanks in advance for the help!
Andy
Andy
Comment