    Ground Fault Protection for traffic gate

    Hello,

    Customer wants to install a new traffic gate with swing arms and security cameras. A 480V, 3phase circuit will feed a step down 480V:120-208V transformer for street lights, security equip, swing gate and general power. The transformer and comm's panel will be on the traffic island. Is the 480V power to the traffic gate require ground fault protection?

    Please advise

    #2
    Requirements for GFCI protection are in section 210.8. Please review and then reply with questions.
    Moderator-Washington State
    Ancora Imparo

    Comment


      #3
      Sorry, lets make sure we are talking about the same thing.
      ground fault protection or ground fault protection for personell? They are not the same
      Moderator-Washington State
      Ancora Imparo

      Comment


        #4
        Originally posted by tom baker View Post
        Sorry, lets make sure we are talking about the same thing.
        ground fault protection or ground fault protection for personell? They are not the same
        yes sorry gfp for personel.other than dwelling units. To be clear the outdoor equipment is a mpz with transformer, low voltage comm's devices including a receptacle will be housed inside an NEMA-3R enclosure.

        The receptacle can be GFP but does the 480V, 3Phase circuit feeding the transformer have to be GFP?

        Comment


          #5
          Originally posted by bravo69 View Post

          yes sorry gfp for personel.other than dwelling units. To be clear the outdoor equipment is a mpz with transformer, low voltage comm's devices including a receptacle will be housed inside an NEMA-3R enclosure.

          The receptacle can be GFP but does the 480V, 3Phase circuit feeding the transformer have to be GFP?
          Nothing in 210.8 requires GFCI protection on a circuit operating over 150 volts to ground. (so far).
          I live for today, I'm just a day behind.

          Comment