If you have a 240/120V, single-phase meter loop attached to a pole where it's overhead to overhead, with only the two phase wires (not the grounded conductor) coming down through the loop to the meter socket, then back up the loop from the meter socket, should, and how should, it be grounded?
Announcement
Collapse
No announcement yet.
Meter Socket Grounding
Collapse
X
-
I'm assuming that the service disconnect is somewhere further down stream? The meter socket and the riser conduits must be bonded to the neutral conductor. I would use an appropriately sized bonding jumper at the weather head from the neutral to a ground clamp on the riser conduit.
This sounds like a coop deal. Are they OK with this?
-
You can't? Usually if the neutral is present it needs to follow the phase leads as far as the service disconnect; off-hand I can't think of a relevant exception.
I do recall years back someone telling me this was common practice on farms.
Comment
-
Senior Member
- Jun 2003
- 11923
- NE (9.06 miles @5.9 Degrees from Winged Horses)
- Electrical Contractor
- Send PM
Originally posted by mobo View PostIf you have a 240/120V, single-phase meter loop attached to a pole where it's overhead to overhead, with only the two phase wires (not the grounded conductor) coming down through the loop to the meter socket, then back up the loop from the meter socket, should, and how should, it be grounded?
If you own it, do it over and bring the grounded conductor down in the meter loop. It does not need to go back up.
We can not have the line and load of that meter socket in the same raceway in this area. . The POCO does not supply up/down loops anymore. Only down, so a separate conduit back up for the load.Tom
TBLO
Comment
-
By grounded you mean connection to a grounding electrode system? NEC does not require, POCO may require. In Wasington we can connect a GEC into the meter socket as its not accessible, however its allowed if the POCO requires.Moderator-Washington State
Ancora Imparo
Comment
-
Originally posted by texie View PostI'm assuming that the service disconnect is somewhere further down stream? The meter socket and the riser conduits must be bonded to the neutral conductor. I would use an appropriately sized bonding jumper at the weather head from the neutral to a ground clamp on the riser conduit.
This sounds like a coop deal. Are they OK with this?
Comment
-
Originally posted by zbang View PostYou can't? Usually if the neutral is present it needs to follow the phase leads as far as the service disconnect; off-hand I can't think of a relevant exception.
I do recall years back someone telling me this was common practice on farms.
Comment
-
Originally posted by ptonsparky View Post
Do you own the meter loop or the POCO?
If you own it, do it over and bring the grounded conductor down in the meter loop. It does not need to go back up.
We can not have the line and load of that meter socket in the same raceway in this area. . The POCO does not supply up/down loops anymore. Only down, so a separate conduit back up for the load.
What is the reason for not wanting the line and load in the same conduit?
Comment
-
Originally posted by tom baker View PostBy grounded you mean connection to a grounding electrode system? NEC does not require, POCO may require. In Wasington we can connect a GEC into the meter socket as its not accessible, however its allowed if the POCO requires.
Comment
-
This also got me thinking.....my brother has a service to an irrigation pump and it's a straight 3-wire, 3-phase service. No grounded conductor. I haven't looked at it yet, but how should that loop be grounded? It's about a 16 ft. loop with the meter socket on it.
Comment
-
Originally posted by mobo View Post
The loop has a #6 bare wire coming out of the meter socket and it is bonded to the pole ground. So wondering if this would be considered kosher as far as grounding?Master Electrician
Electrical Contractor
Richmond, VA
Comment
-
Originally posted by mobo View Post
What's the reason/logic for not allowing loops?Moderator-Washington State
Ancora Imparo
Comment
-
Originally posted by mobo View PostThis also got me thinking.....my brother has a service to an irrigation pump and it's a straight 3-wire, 3-phase service. No grounded conductor. I haven't looked at it yet, but how should that loop be grounded? It's about a 16 ft. loop with the meter socket on it.Moderator-Washington State
Ancora Imparo
Comment
Comment