    CEE

    If a properly installed CEE is present and there are no other electrodes present does the CEE need to be supplemented?

    Thank you.



    #2
    No, concrete encased electrode can stand alone. Only the water pipe needs to be supplemented
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky

    Comment


      #3
      Originally posted by Dennis Alwon View Post
      No, concrete encased electrode can stand alone. Only the water pipe needs to be supplemented
      Is that stated in 250.50?

      Im trying to find the code verbage that tells me that.

      Comment


        #4
        Originally posted by nizak View Post

        Is that stated in 250.50?

        Im trying to find the code verbage that tells me that.
        See 250.53(A)(2)

        Comment


          #5
          Originally posted by Dennis Alwon View Post
          No, concrete encased electrode can stand alone. Only the water pipe needs to be supplemented
          And rod or pipe electrodes unless you can prove they are 25 ohms or less.

          I live for today, I'm just a day behind.

          Comment