    GEC attachment

    is it a violation to attach a GEC to a service disconnect by means of a mechanical lug to the enclosure exterior?

    I have got two 100 amp disconnects that have no allowance to attach any more conductors to the factory neutral assembly inside.
    Poco will not allow GEC to terminate in meter base that the disconnects feed from.

    Rewiiring half of a duplex and found there was never a grounding electrode system installed when it was built in 1968.

    Looking for a compliant fix without reworking the entire service.

    thanks

    #2
    250.24 says you have to land your gec at the neutral.
    If Billy Idol is on your playlist go reevaluate your life.

    Comment


      #3
      Move the equipment ground to the lug bolted to the enclosure, and put the GEC in its place on the neutral bar.

      Comment


        #4
        Couldn't the GEC be connected directly to the neutral conductor in the disconnect?
        Rob

        Moderator

        All responses based on the 2017 NEC unless otherwise noted

        Comment


          #5
          Originally posted by infinity View Post
          Couldn't the GEC be connected directly to the neutral conductor in the disconnect?
          I have done that before, use what what we used to call "gutter tap" connectors - a lay in type lug with a second lug for the tap conductor.
          I live for today, I'm just a day behind.