Smallest EGC in Indoor Hot Tub Circuit
cnodad
I'm looking at installing a heater for a spa in a single family dwelling. The heater requires a 15 Amp GFCI protected circuit. No problem there. My question is whether or not I can use 14/2 Romex to install the circuit or if I have to bump to 12/2 to get a larger EGC.
charlie b
Lockport, IL
Retired Electrical Engineer
The size of the EGC is determined on the basis of the circuit breaker's rating. 15 amp circuit = 14 awg (copper) EGC.
JohnJ0906
Baltimore, MD
Is there something in the instructions that require a #12 minimum EGC?
cnodad
Not in the instructions, no. I'm a rookie at pools and spas, so I'm still developing judgment there. I look around in 680 and I see "not smaller than 12 AWG" in a bunch of places, and I wonder if I'm missing something about indoor installations.
JohnJ0906
Baltimore, MD
Is this a hot tub/spa, or a hydromassage tub?
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
Art. 680.43 tells us to wire an indoor hot tub per Parts I and II.
If we go to part II art. 680.21 (A)(1) It tells us a minumum of #12 for the EGC to any pool associated motor. I realize this is not a pool but the hot tub section says to follow Part II-- IMO you need #12
JohnJ0906
Baltimore, MD
I agree with Dennis, and want to add - insulated EGC.
If this is actually a hydromassage Tub, a #14 would be OK.
(I hear "hot tub" used as slang for what is actually a hydromassage tub around here, which is why I asked the OP)
cnodad
I guess by 2008 definitions it would be either a "Self-Contained Spa or Hot Tub" or a "Self-Contained Therapeutic Tub or Hydrotherapeutic Tank"
It is a bathtub with a pump motor and a field installed heater.
cnodad
I saw 680.21, which would require a #12 for a 15 amp circuit, but this is for a heater, so doesn't apply? (I'm asking)
680.43 also says that you can use any wiring method covered by Chapter 3 (which would include Romex, right?)
Dennis Alwon
Chapel Hill, NC
Good point- the op may actually have a hydromassage tub. I always pull a #12 anyway--- force of habit.
JohnJ0906
Baltimore, MD
680.43 is for outdoor installations, if I'm not mistaken. And 680.42(C) is for interior wiring to outdoor installations.
So it doesn't really cover this situation... but it is because of sections like that that I'm asking.
What NEC are you using?
The '08 on my lap right now has 680.43 Indoor Installations
Dennis Alwon
Chapel Hill, NC
Not in the 2008 or 2005 NEC 680. 43 is indoor. 680.42(C) is for interior wiring to an outdoor installation
rcarroll
I would consider this to be a hydromassage bathtub. See the definition in 680.2. So, 680.70 thru 680.74 would apply.
Dennis Alwon
Chapel Hill, NC
You posted this at the same time I was posting-- I never saw it-- I agree this is a hydromassage tub.