Hello all,
We have a friend in the air conditioning business that recently installed a few rooftop cooling only carrier units on a school. The units are tripping in the VFD drive on a earth ground fault. The electrican that wired the school swears the grounding system is up to code. I haven't looked at the system yet. The VFD in the AC units is a ABB drive and the president of ABB says there is not another drive in the country that trips on this fault for any other reason than a faulty grounding system. The roof units are on the 2nd floor, 200 ft from the Main Distribution Panel on the
1st floor. We have a clamp on earth ground resistance meter to test electrode resistance and were planning on running a temporary wire from the AC unit to the MDP to test the resistance on the permanent ground. Anyone got any other suggestions?
Thanks in advance guys,
Alan
We have a friend in the air conditioning business that recently installed a few rooftop cooling only carrier units on a school. The units are tripping in the VFD drive on a earth ground fault. The electrican that wired the school swears the grounding system is up to code. I haven't looked at the system yet. The VFD in the AC units is a ABB drive and the president of ABB says there is not another drive in the country that trips on this fault for any other reason than a faulty grounding system. The roof units are on the 2nd floor, 200 ft from the Main Distribution Panel on the
1st floor. We have a clamp on earth ground resistance meter to test electrode resistance and were planning on running a temporary wire from the AC unit to the MDP to test the resistance on the permanent ground. Anyone got any other suggestions?
Thanks in advance guys,