I'm pulling 120V control wiring in an existing conduit at a local winery for valving to modulate glycol for temp. control on fermentation tanks and noticed the EGC has almost completely melted off. The conduit and junction boxes are all PVC. The circuits are all fed from a nearby PLC panel- 10 amp IEC breakers. When I pulled the cover off the first box the ground wires were melted into the cover and the insulation was gone. Any ideas on what could have happened? Nobody on site remembers ever having a problem with any associated equipment. If a ground fault large enough to completely melt the insulation off a 14ga thhn conductor, why didn't it trip any OCPD's? Where is the evidence of such a fault? (other than the wire) It is a temp controlled damp environment and I noticed cold air is traveling from the NM flex connecting the valve into the junction box where splicing is made. (typical for two valves each at 12 tanks) Two of the tanks are near large roll up doors, which are opened for maintenance purposes. The only thing I can come up with as a cause is excessive condensation in the junction boxes, perhaps in summer months when the doors are open. As for now I'm planning on duct sealing the conduits and using wet location wire nuts. Any ideas???? Thanks for your input.