senario
13.8KV underground feed to a motor with PVC conduit in a duct bank. 90degree Elbows and stubups are HDGS, and vertical rise is HDGS. Last 4 to 6 feet is LFMC to the motor terminal box. LFMC is 6" liquid tight. A separate ground conductor is run with the power feeds inside the conduit. Installation is in an electrical Non-Hazardous area.
Question;
Is it required to install an external bonding jumper across the liquid tight flexible metal conduit? Or, is the internal separate ground wire satisfactory?
I believe there are 2 separate issues.
1. Provide ground fault return path. The internal ground wire provides this path.
2. Make sure the conduit is electrically continuous and grounded. Can the LFMC internal ground make the lower HDGS conduit electrically continous? Note, motor terminal box has a ground conductor down to the ground grid. Switchgear is also connected to same ground grid as well as upstream transformer neutral.
13.8KV underground feed to a motor with PVC conduit in a duct bank. 90degree Elbows and stubups are HDGS, and vertical rise is HDGS. Last 4 to 6 feet is LFMC to the motor terminal box. LFMC is 6" liquid tight. A separate ground conductor is run with the power feeds inside the conduit. Installation is in an electrical Non-Hazardous area.
Question;
Is it required to install an external bonding jumper across the liquid tight flexible metal conduit? Or, is the internal separate ground wire satisfactory?
I believe there are 2 separate issues.
1. Provide ground fault return path. The internal ground wire provides this path.
2. Make sure the conduit is electrically continuous and grounded. Can the LFMC internal ground make the lower HDGS conduit electrically continous? Note, motor terminal box has a ground conductor down to the ground grid. Switchgear is also connected to same ground grid as well as upstream transformer neutral.