    Is switch is recessed in gyp wall what would you use as your LV wiring from switch to ceiling? LV cable with a conduit stub up? Can't use MC cable as that's 600v, correct?
    Attached Files

    #2
    You can use MC. It's for up to 600 volts but I would do conduit and then run CL3/CL2 riser rated 16-2 or 14-2 stranded cabling.


    Sent from my iPhone using Tapatalk

    Comment


      #3
      Originally posted by blkmagik21 View Post
      You can use MC. It's for up to 600 volts but I would do conduit and then run CL3/CL2 riser rated 16-2 or 14-2 stranded cabling.


      Sent from my iPhone using Tapatalk
      Why would you do conduit? Thanks.

      Comment


        #4
        Originally posted by mstrlucky74 View Post
        Why would you do conduit? Thanks.
        Maybe he's a transplant from Chicago.

        Comment


          #5
          Everything south of the "power pack" is LV CL2 wiring. Nothing says that you couldn't use MC to the switch but why would you? Thermostat wire would be fine, either dropped down the partition or in a stub up conduit from the switch box into the ceiling.

          -Hal

          Comment


            #6
            Originally posted by hbiss View Post
            Everything south of the "power pack" is LV CL2 wiring. Nothing says that you couldn't use MC to the switch but why would you? Thermostat wire would be fine, either dropped down the partition or in a stub up conduit from the switch box into the ceiling.

            -Hal
            Yes but the wire has to be protected within the wall by conduit or an armored cable like MC. Can't just run tstat wire or any other wire down the wall. So my question is why a conduit stub instead of MC cable? I think MC would be quicker.

            Comment


              #7
              Originally posted by mstrlucky74 View Post
              Yes but the wire has to be protected within the wall by conduit or an armored cable like MC. [COLOR="#FF0000"]Can't just run tstat wire or any other wire down the wall[/COLOR]. So my question is why a conduit stub instead of MC cable? I think MC would be quicker.
              Sez who? What's the diff with that and Romex?

              Comment


                #8
                Yes but the wire has to be protected within the wall by conduit or an armored cable like MC.
                Sez who? Not the NEC. If your job specs call for it, it's customary to run conduit from the box up into the ceiling (stub up) and pull a CL2 cable into it. What are you doing with the data and communication drops?

                -Hal

                Comment


                  #9
                  Originally posted by mstrlucky74 View Post
                  Why would you do conduit? Thanks.
                  Most commercial building require emt stub ups for low voltage. If it's not required on your project then just run 16-2 stranded CL2/CL3 Riser rated UL listed wire.

                  With low voltage power circuits stranded wire is always recommended as it has more throughout than solid wire of the same size. Especially in lower voltages.


                  Sent from my iPhone using Tapatalk

                  Comment


                    #10
                    Originally posted by blkmagik21 View Post

                    With low voltage power circuits stranded wire is always recommended as it has more throughout than solid wire of the same size. Especially in lower voltages.
                    What??

                    -Hal

                    Comment


                      #11
                      Originally posted by hbiss View Post
                      What??

                      -Hal
                      Electricity doesn't flow through copper, it flows on the surface of copper. Therefor stranded 16 AWG wire has more surface wire on all the individual strands than a solid wire of the same size. This is called the skin effect in electrical theory books.


                      Sent from my iPhone using Tapatalk

                      Comment


                        #12
                        Wiring Method LV Swith

                        Comment


                          #13
                          Originally posted by blkmagik21 View Post
                          Electricity doesn't flow through copper, it flows on the surface of copper. Therefor stranded 16 AWG wire has more surface wire on all the individual strands than a solid wire of the same size. This is called the skin effect in electrical theory books.


                          Sent from my iPhone using Tapatalk
                          No, stranded wire has the same issue as solid, unless it is Litz wire, plus in the same gauge size it has very slightly lower total cross sectional area. The [COLOR="#FF0000"]skin effect[/COLOR] is the result of back EMF generated by AC at the interior of the cable, solid or stranded. On yet another hand, the skin depth for copper at 60 Hz is given as 8.5 mm, so for the conductors in play here, negligible. For DC there is no skin effect. And you couldn't pay me enough to do any significant amount of wiring with stranded, it's just such a PITA.

                          Comment


                            #14
                            Originally posted by blkmagik21 View Post
                            Electricity doesn't flow through copper, it flows on the surface of copper. Therefor stranded 16 AWG wire has more surface wire on all the individual strands than a solid wire of the same size. This is called the skin effect in electrical theory books.


                            Sent from my iPhone using Tapatalk
                            A gross oversimplification, as indicated in previous comment. The only place the current would flow only in the surface layer would be in the case of a superconductor. Flows *near* the surface makes for a much better statement.

                            Sent from my XT1585 using Tapatalk

                            Comment


                              #15
                              It's also very much frequency dependent. At 60hz skin effect is for all practical purposes non-existent. You would have to get up into RF to see it.

                              -Hal

                              Comment