    Originally posted by Fulthrotl View Post
    oh. got it. sorry.
    to the original poster:

    send lots of RFI's. to the people you have the contract with, instead of us.
    hope that helps.
    dont pay attention to that other guy..😜... the feedback you gave is what I was looking for. Thanks

    Comment


      #17
      Originally posted by mstrlucky74 View Post
      About 8'. That's a good thought. Just have to make sure that span could support xfrmr.
      If you use 3" Unistrut I doubt you'd have a problem. Their manual says with a span of 8 ft the maximum uniform load is 1,310 lb. The transformer will be more like a point load, and it makes a difference if it's near one end or in the middle, so you'd have to go to the manual and do some calculations.