Existing Electric Baseboard?

Status
Not open for further replies.

Jerseydaze

Senior Member
I am direct replacing some baseboard heat .
The Math comes to a little over 19 amps at 240v I know it should be 80% on a 20 amp circuit.
Am I doing the wrong thing by simply changing the baseboards or should I try to split up run new circuits ect?
 

JFletcher

Senior Member
Location
Williamsburg, VA
I am direct replacing some baseboard heat .
The Math comes to a little over 19 amps at 240v I know it should be 80% on a 20 amp circuit.
Am I doing the wrong thing by simply changing the baseboards or should I try to split up run new circuits ect?

Fixed heating should only be at 80% of the circuit's ampacity as it's a continuous load. I'm guessing you're around 4600W on a 20A circuit (which is 'a little over 19A')?

Can you install slightly smaller heaters to get under 16A on a 20A breaker? I'd do that before rewiring.
 

kwired

Electron manager
Location
NE Nebraska
Fixed heating should only be at 80% of the circuit's ampacity as it's a continuous load. I'm guessing you're around 4600W on a 20A circuit (which is 'a little over 19A')?

Can you install slightly smaller heaters to get under 16A on a 20A breaker? I'd do that before rewiring.
Or find a way to get a new circuit to some heaters. Just one or two of them is likely all that need separated from the others to get the load down enough.
 