mstrlucky74
Senior Member
- Location
- NJ
Looks like this #6 ground wire is run without conduit. What type of insulation would be needed? Thanks.
PVC coated RGS for the conduit?
Since it can also be bare any insulation will do. If it's colored then not white or gray.
And 3/4" x 10' rod. Someone wants to throw money away.
So you can run bare or thhn in direct contact with earth?
Why exactly is it a waste?
Why exactly is it a waste?
The ground rod is not required per NEC (and is stupid) so i think you can do whatever you want with it, as long as its done per the plans.
It's a waste because look at the size of that huge concrete electrode that's buried in the ground compared to the rod.
I kind of disagree with you guys. Not in theory but in practice.
The NEC is not a design manual, it is a set of minimum safety standards. These drawings are engineering specs of how they want the light pole installed.
It may be a waste of money but that's not up to the electrician. The electrician must install according to job specs.
I kind of disagree with you guys. Not in theory but in practice.
The NEC is not a design manual, it is a set of minimum safety standards. These drawings are engineering specs of how they want the light pole installed.
It may be a waste of money but that's not up to the electrician. The electrician must install according to job specs.
I kind of disagree with you guys. Not in theory but in practice.
The NEC is not a design manual, it is a set of minimum safety standards. These drawings are engineering specs of how they want the light pole installed.
It may be a waste of money but that's not up to the electrician. The electrician must install according to job specs.
Looks like this #6 ground wire is run without conduit. What type of insulation would be needed? Thanks.
I always used copper solid...I also always used #4
Same reasons to use PVC coated RMC and cadweld#4 to a rod? Why?
#4 to a rod? Why?
Same reasons to use PVC coated RMC and cadweld