    Riser Tap

    Someone else is running the #600 riser. We are just running from the tap box to the panel( we are doing the tap). This happens at about 5 floors. I know of the Ilsco “port” type taps but couldn’t the piercing type be used to and eliminate the need to cut wires? Actually not sure the crimping type will work as I'm tapping #600 to #6 and they don't list that size range. Thanks.
    Attached Files
    Last edited by mstrlucky74; 04-16-19, 03:04 PM.

    #2
    What is your question?

    Comment


      #3
      Yes insulation piercing taps will work if you can find them in the correct range.
      Last edited by infinity; 04-16-19, 08:59 PM. Reason: Fixed Error
      Rob

      Moderator

      All responses based on the 2017 NEC unless otherwise noted

      Comment


        #4
        My other question. If you used a ported tap block you would have to cut the wire where your making the tap. If using insulation piercing you would not need to cut wire. Wouldn't you want to avoid cutting wire and jut pull wire point to point? Thanks

        Comment


          #5
          You either have to cut it or feed it through the tap if the hole is large enough to allow the insulated conductor to pass through.
          Rob

          Moderator

          All responses based on the 2017 NEC unless otherwise noted

          Comment


            #6
            Originally posted by infinity View Post
            You either have to cut it or feed it through the tap if the hole is large enough to allow the insulated conductor to pass through.
            Your referring to these that the wire can be feed straight thru?

            https://commerce.ilsco.com/e2wShoppi...512:3100012872

            Comment


              #7
              Originally posted by mstrlucky74 View Post
              Your referring to these that the wire can be feed straight thru?

              https://commerce.ilsco.com/e2wShoppi...512:3100012872
              Yes if the hole is larger enough for the insulated conductor to pass through but since the riser will be installed by someone else that won't work for you. I would use insulation piercing taps if you cannot find the proper wire range you might need to make your tap conductors a bit larger.
              Rob

              Moderator

              All responses based on the 2017 NEC unless otherwise noted

              Comment


                #8
                Does anyone have a link for the piercing tap connectors?

                Comment


                  #9
                  https://idealind.com/shop/btc500-14.html
                  At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

                  Comment


                    #10
                    Thanks

                    Sent from my SM-N960U using Tapatalk

                    Comment


                      #11
                      Would bus detail make sense instead of tap? Someone mentioned there might not be room for the taps connectors. Not sure that makes sense. The box would have to be sized for conduits entering top and bottom and also entering the right side, correct?

                      Sent from my SM-N960U using Tapatalk

                      Comment


                        #12
                        Originally posted by mstrlucky74 View Post
                        Would bus detail make sense instead of tap? Someone mentioned there might not be room for the taps connectors. Not sure that makes sense. The box would have to be sized for conduits entering top and bottom and also entering the right side, correct?
                        Bus detail for a #6 tap? Probably not. Yes the box needs to be sized for the riser conduits regardless of whether or not you use bus detail.
                        Rob

                        Moderator

                        All responses based on the 2017 NEC unless otherwise noted

                        Comment


                          #13
                          I didn't see one that has a #600 run and a #6 tap.

                          Comment