    Elevator Main Disconnect

    I am adding some lights and GFI's on an elevator shaft due to motor controller upgrade. The elevator inspector is asking me to change the existing disconnect which is a 3 phase fusible 240 volts disconnect to a Heavy Duty one. Any one heard about this requirement? Motor is 7 1/2 HP and will be reuse. Label amps says 20.5 @ 208 volts
    Miguel

    All things, therefore, that you want men to do to you, you also must likewise do to them

    #2
    To me, the what-was-compliant-when-installed clause ought to apply.

    But, then, I'm inexperienced with elevator-specific installations, so . . .
    Master Electrician
    Electrical Contractor
    Richmond, VA

    Comment


      #3
      The existing switch may not be horsepower rated.

      see https://forums.mikeholt.com/showthread.php?t=142331
      The more they overthink the plumbing, the easier it is to stop up the drain