Is it a PIA to splice through 12/4 in device box? Case in point, if you have 3 receptacles next to each other all on separate ckt and allowed to share neutral and you pull a 12/4 to the first device.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
It depends on the cu. in of your box but it will be tight. You may be able to if your box has a minumum 27 cu.in. This allows a 12/4 and a 12/3 with a device grounds and a clamp-- not sure what you are using. Personally I would avoid it and put a jb above, if possible
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
3 gang box? Talking about 3 receptacles a few feet apart. So 4x2-1/8 box for each recept.

Well, cubic inches aren't the problem. With a plaster ring you've got more than 32 - 33 cubes and, by my count, you need 25.

Are you pigtailing, or landing a lot of conductors on the device?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Is it a PIA to splice through 12/4 in device box? Case in point, if you have 3 receptacles next to each other all on separate ckt and allowed to share neutral and you pull a 12/4 to the first device.

That is how I would do it.
 