    MC Cable Wiring

    If separate neutrals are required and wiring a job in MC cable are you better off using a separate 12/2 for each receptacle circuit or a multiple neutral MC cable? I would think multiple neutral cable would save a lot on qty. of cable although.

    #2
    Originally posted by mstrlucky74 View Post
    If separate neutrals are required and wiring a job in MC cable are you better off using a separate 12/2 for each receptacle circuit or a multiple neutral MC cable? I would think multiple neutral cable would save a lot on qty. of cable although.
    It also multiplies the number of joints you have to make in every box. In my opinion, 12/2 costs less to use, especially with labor in the equation.

    t may even cost less per foot per circuit in materials alone.
    Master Electrician
    Electrical Contractor
    Richmond, VA

    Comment


      #3
      We would use a 12/2 for each circuit.
      Rob

      Moderator

      All responses based on the 2017 NEC unless otherwise noted

      Comment


        #4
        Originally posted by infinity View Post
        We would use a 12/2 for each circuit.
        Why instead of multiple neutral MC?

        Comment


          #5
          Originally posted by mstrlucky74 View Post

          Why instead of multiple neutral MC?
          It's just easier to pull 12/2 instead of 12/4/4 and with 12/4/4 you have to somehow carry through the other 3 circuits which can lead to wiring errors. IMO it's just not worth it unless your plan is run the 12/4/4 to a big homerun box in the ceiling and then distribute from there. To run that out to a receptacle or switch box just isn't a good plan.
          Rob

          Moderator

          All responses based on the 2017 NEC unless otherwise noted

          Comment


            #6
            Originally posted by infinity View Post

            It's just easier to pull 12/2 instead of 12/4/4 and with 12/4/4 you have to somehow carry through the other 3 circuits which can lead to wiring errors. IMO it's just not worth it unless your plan is run the 12/4/4 to a big homerun box in the ceiling and then distribute from there. To run that out to a receptacle or switch box just isn't a good plan.
            Thank you.