    Emergency circuits in healthcare facility

    Is it code to use conduit for emergency circuits in a healthcare facility? Thank

    Sent from my SM-N960U using Tapatalk


    #2
    Read 517.30(C)(3)

    Roger
    Moderator

    Comment


      #3
      517.31(C)(3)

      Comment


        #4
        Originally posted by coffeebean View Post
        517.31(C)(3)
        Only if your area has already adopted the 2017.

        Roger
        Moderator

        Comment


          #5
          Originally posted by roger View Post
          Read 517.30(C)(3)

          Roger
          Well seems to me that hospital grade MC is NOT allowed for EM circuits.

          (3) Mechanical Protection of the Emergency System.
          The wiring of the emergency system in hospitals shall be
          mechanically protected. Where installed as branch circuits
          in patient care areas, the installation shall comply with the
          requirements of 517.13(A) and (B). The following wiring
          methods shall be permitted:
          (1) Nonflexible metal raceways, Type MI cable, or Schedule
          80 PVC conduit. Nonmetallic raceways shall not be
          used for branch circuits that supply patient care areas.
          (2) Where encased in not less than 50 mm (2 in.) of concrete,
          Schedule 40 PVC conduit, flexible nonmetallic
          or jacketed metallic raceways, or jacketed metallic
          cable assemblies listed for installation in concrete.
          Nonmetallic raceways shall not be used for branch circuits
          that supply patient care areas.
          (3) Listed flexible metal raceways and listed metal
          sheathed cable assemblies in any of the following:
          a. Where used in listed prefabricated medical headwalls
          b. In listed office furnishings
          c. Where fished into existing walls or ceilings, not otherwise
          accessible and not subject to physical damage
          d. Where necessary

          Comment


            #6
            Originally posted by mstrlucky74 View Post

            Well seems to me that hospital grade MC is NOT allowed for EM circuits.
            You are correct.

            Roger

            Moderator

            Comment