    Conduit Stub Up

    So drawings call for 2” conduit stub up from tele/data outlet. Is there even a 4” box that has 2” k/o? Can’t find one? Thanks.

    #2
    Maybe just use a deep 4" box with no premade knockouts and punch your own, such as this one https://www.garvinindustries.com/ele...xes/52181-blnk
    Ron

    Comment


      #3
      How could it even fit hen most boxes are 2-1/8 deep?

      Comment


        #4
        Originally posted by horsegoer View Post
        How could it even fit hen most boxes are 2-1/8 deep?
        Look closer at the link that Ron supplied. The box shown is 3-1/2" deep by 4" square.
        Another Al in Minnesota

        Comment


          #5
          Originally posted by al hildenbrand View Post

          Look closer at the link that Ron supplied. The box shown is 3-1/2" deep by 4" square.
          Thanks I didnt look yet when I posted. Look like you have to ko yourself.

          Comment


            #6
            These have concentric KO's up to 2":

            https://www.platt.com/platt-electric...px?zpid=910502

            Rob

            Moderator

            All responses based on the 2017 NEC unless otherwise noted

            Comment


              #7
              Originally posted by infinity View Post
              These have concentric KO's up to 2":

              Nice

              Ron

              Comment


                #8
                ...and >3< grounding screws! No need for pigtails!

                Comment


                  #9
                  Originally posted by PaulMmn View Post
                  ...and >3< grounding screws! No need for pigtails!
                  For cat 6 cables.