Anyone know if a feeder is required to be 2 hour fire protected and it's run outdoor does the still requires some sort of 2 hour fire protection? This is for NYC? THanks
Announcement
Collapse
No announcement yet.
2 Hour Feeders Fire Protection
Collapse
X
-
General rules (chapter 1-4) not required.
Can't think of any special rules in NEC but could see there being that possibility in certain situations,maybe in particular for some emergency systems.
I live for today, I'm just a day behind.
Comment
-
-
Originally posted by horsegoer View Post
Kwired....general rules chapter 1-4??? NEC.
I am not aware of any 2 hour requirement for a feeder circuit in chapters 1-4, not aware of any in 5-7 either. But those are sections that are more specific application sections and there could be something I don't encounter very often (or ever) that could have requirements I am not aware of. If you have a specific installation that is covered by chapters 5-7 then be sure to read through the appropriate section carefully to find out or at least ask some questions about a specific application.
You mentioned emergency side feeders - first make sure what you are calling emergency is same thing NEC would call emergency. Optional standy systems are not emergency systems when using NEC terminology.I live for today, I'm just a day behind.
Comment
-
Originally posted by kwired View Post
What is meant by that is the way NEC works is chapters 1-4 are general rules that apply to pretty much everything unless specifically addressed for specific situations that are covered in chapters 5-7.
I am not aware of any 2 hour requirement for a feeder circuit in chapters 1-4, not aware of any in 5-7 either. But those are sections that are more specific application sections and there could be something I don't encounter very often (or ever) that could have requirements I am not aware of. If you have a specific installation that is covered by chapters 5-7 then be sure to read through the appropriate section carefully to find out or at least ask some questions about a specific application.
You mentioned emergency side feeders - first make sure what you are calling emergency is same thing NEC would call emergency. Optional standy systems are not emergency systems when using NEC terminology.
Comment
-
Originally posted by horsegoer View Post
Thanks. So there is EM, optional stand-by and life safety or just emergency and optional standby? TRob
Moderator
All responses based on the 2017 NEC unless otherwise noted
Comment
-
Originally posted by infinity View Post
Look at the NYC amendments. There is no Article 701 so you're left with Article 700 and 702.
https://www1.nyc.gov/assets/building...l111of2013.pdfRon
Comment
-
Originally posted by ron View PostIn case NYC BS wasn't complicated enough, Local Law 111 of 2013 reinstated Article 701
https://www1.nyc.gov/assets/building...l111of2013.pdfRob
Moderator
All responses based on the 2017 NEC unless otherwise noted
Comment