    Lighting pole grounding in concrete medians

    Hi all, my apologizes if this question has been asked.

    I'm doing some work in Ontario where new metal lighting poles on concrete bases are being mounted in a concrete median.
    I cannot seem to find any related documents stating every lighting pole needs a ground rod placed next to it, but I have read over and over that every pole needs a ground rod (lightning protection maybe?). If they are in fact required, how would they be mounted in the concrete? Do I install a handwell adjacent to the pole to allow for connections and testing?

    Any help would be greatly appreciated.

    Regards,

    #2
    I moved this to the Canadian forum. In the US there is no need for a ground rod at every pole. It is often done but it is not required. Hopefully some Canadians will reach out. [MENTION=83316]electricguy[/MENTION] [MENTION=159332]Eddy_Current[/MENTION] [MENTION=159339]daveEM[/MENTION]
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky

    Comment


      #3
      Originally posted by EastCanadian View Post
      Hi all, my apologizes if this question has been asked.

      I'm doing some work in Ontario where new metal lighting poles on concrete bases are being mounted in a concrete median.
      I cannot seem to find any related documents stating every lighting pole needs a ground rod placed next to it, but I have read over and over that every pole needs a ground rod (lightning protection maybe?). If they are in fact required, how would they be mounted in the concrete? Do I install a handwell adjacent to the pole to allow for connections and testing?

      Any help would be greatly appreciated.

      Regards,
      Lightning protection is not required for each pole.
      Every pole needs to be bonded back to the source, with proper grounding at the source.
      ESA has a streetlighting guide online. https://www.esasafe.com/assets/files...r2-May2015.pdf
      If you happen to get the work, they also have a guide for Traffic pole/controller bonding as well.

      If you did require a ground rod at any pole, I would just bond to rebar in the concrete base.

      Comment


        #4
        Originally posted by 414Mhz View Post
        If you did require a ground rod at any pole, I would just bond to rebar in the concrete base.
        Wouldn't you want the circuit EGC to be part of that connection?
        Master Electrician
        Electrical Contractor
        Richmond, VA

        Comment


          #5
          Originally posted by LarryFine View Post
          Wouldn't you want the circuit EGC to be part of that connection?
          We don't have EGC's here

          But yes, any supplemental ground rods installed beyond the source, you would bond to the ground wire.

          Comment


            #6
            Originally posted by 414Mhz View Post
            We don't have EGC's here

            But yes, any supplemental ground rods installed beyond the source, you would bond to the ground wire.
            Perfect!
            Thank you so much for the help team!!