    Control panel for VFDs

    Hello,

    Is it typical to house VFD in an external enclosure for Nema 1 or IP21 rated VFDs? I've got control relays and some reset PBs that I need to locate in a control panel in addition to control transformer. It sounds like putting the VFD and aux. devices in a control panel/enclosure makes sense and provides additional protection.

    Thanks,
    EE

    #2
    Make sure there is sufficient ventilation is main thing.

    Doesn't necessarily need to be a powered vent, but if you trap too much heat in your enclosure drive will trip on high temp limit.
    I live for today, I'm just a day behind.

    Comment


      #3
      Originally posted by FaradayFF View Post
      Hello,

      Is it typical to house VFD in an external enclosure for Nema 1 or IP21 rated VFDs? I've got control relays and some reset PBs that I need to locate in a control panel in addition to control transformer. It sounds like putting the VFD and aux. devices in a control panel/enclosure makes sense and provides additional protection.

      Thanks,
      EE
      very typical.