New vs Older vfd

Learn the NEC with Mike Holt now!
Status
Not open for further replies.
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Just a heads up.

Customer called to complain his replacement VFD was tripping the Pushmatic breaker. We had put in a larger breaker when the previous drive was first installed. Well, turns out the previous drive only had to be sized about twice up for single phase input. New one requires four times up. This drive input is rated at 68 amps three phase. We only have a 70 amp single phase service to the building. It is what it is for the moment.

Tech support says new models have smaller capacitors so they have to be upsized 3-4 times vs the 2 it used to be.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Just a heads up.

Customer called to complain his replacement VFD was tripping the Pushmatic breaker. We had put in a larger breaker when the previous drive was first installed. Well, turns out the previous drive only had to be sized about twice up for single phase input. New one requires four times up. This drive input is rated at 68 amps three phase. We only have a 70 amp single phase service to the building. It is what it is for the moment.

Tech support says new models have smaller capacitors so they have to be upsized 3-4 times vs the 2 it used to be.
Well, it's not actually "smaller" caps in terms of capacity, it's that they are made to get more capacitance in a smaller can in order to make a smaller drive package, but that means they will over heat more easily when being used on high ripple applications such as converting single phase. 4x is pretty extreme from my experience, but I've seen it listed as a 65% de-rate, meaning using at 35% of rated when feeding with single phase (assuming a drive that is not designed for single phase input), so that's pretty close to 3x over sizing. If you use a VFD that has a built-in DC bus choke, you can go back to a 50% de-rate. But that usually only comes on the high-end drives.
 

Dzboyce

Senior Member
Location
Royal City, WA
Occupation
Washington 03 Electrician & plumber
That’s what I have seen with vfd’s on 5 hp 3 phase submersible motors.

A franklin or Pentair drive designed for single phase in and three phase out, will only require a 50 or 60 amp breaker.

However a Yaskawa being used as single phase in and three phase out will require an 80 amp breaker. This is because of having to oversize the VFD as you mentioned.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Yeah, because most Asian drives don’t have DC bus chokes. Capacitors are cheap for Asian drive mfrs since most caps are made by the same companies. Big chunks of steel wrapped with copper wire (aka chokes) are expensive to ship from Asia.
 

paulengr

Senior Member
The latest crop of Schneider (TMEIC) drives have DC bus chokes available and the pricing is comparable to the low cost brands. Might look at the price of a 312 or 630 series.

Sent from my SM-T350 using Tapatalk
 