    Hi Everyone,

    Dose anyone know where in the 2008 NEC it talks about NEMA in Enclosures and/or boxes? More specifically talking about NEMA boxes and motors.

    Thanks,

    Daniel

    #2
    You will only find NEMA references in Informational notes / Fine print notes which are not part of the code itself.

    Comment


      #3
      Check out Section 110.20 of the 2008 NEC. The enclosure-type numbers are from NEMA. The section and table was moved from 430.91 in the 2005 NEC.
      Bryan P. Holland, MCP
      NEMA - Codes & Standards

      Comment


        #4
        Originally posted by danielbates7 View Post
        Hi Everyone,

        Dose anyone know where in the 2008 NEC it talks about NEMA in Enclosures and/or boxes? More specifically talking about NEMA boxes and motors.

        Thanks,

        Daniel
        NEMA enclosure ratings are described here:
        https://www.nema.org/Products/Docume...sure-types.pdf

        Executive summary:
        NEMA1 = indoors
        NEMA3R = outdoors and in a specific orientation, usually upright
        NEMA4 = outdoors and in any orientation
        NEMA4X= like NEMA4, but also rust proof

        Comment


          #5
          Originally posted by bphgravity View Post
          Check out Section 110.20 of the 2008 NEC. The enclosure-type numbers are from NEMA. The section and table was moved from 430.91 in the 2005 NEC.
          Did you mean 110.28? Maybe it was moved since 2008, 110.28 in 2014 does have table like you described, and sounds like what OP may be looking for.
          I live for today, I'm just a day behind.

          Comment


            #6
            Originally posted by kwired View Post
            Did you mean 110.28? Maybe it was moved since 2008, 110.28 in 2014 does have table like you described, and sounds like what OP may be looking for.
            Since the OP asked the question specifically for the 2008 cycle, Bryan answered with the correct section number and it was 110.20.

            Roger
            Moderator

            Comment


              #7
              Yes, it moved again in the 2011 NEC to 110.28.
              Bryan P. Holland, MCP
              NEMA - Codes & Standards