    replied
    Yes, it moved again in the 2011 NEC to 110.28.

    Leave a comment:


  • roger
    replied
    Originally posted by kwired View Post
    Did you mean 110.28? Maybe it was moved since 2008, 110.28 in 2014 does have table like you described, and sounds like what OP may be looking for.
    Since the OP asked the question specifically for the 2008 cycle, Bryan answered with the correct section number and it was 110.20.

    Roger

    Leave a comment:


  • kwired
    replied
    Originally posted by bphgravity View Post
    Check out Section 110.20 of the 2008 NEC. The enclosure-type numbers are from NEMA. The section and table was moved from 430.91 in the 2005 NEC.
    Did you mean 110.28? Maybe it was moved since 2008, 110.28 in 2014 does have table like you described, and sounds like what OP may be looking for.

    Leave a comment:


  • Carultch
    replied
    Originally posted by danielbates7 View Post
    Hi Everyone,

    Dose anyone know where in the 2008 NEC it talks about NEMA in Enclosures and/or boxes? More specifically talking about NEMA boxes and motors.

    Thanks,

    Daniel
    NEMA enclosure ratings are described here:
    https://www.nema.org/Products/Docume...sure-types.pdf

    Executive summary:
    NEMA1 = indoors
    NEMA3R = outdoors and in a specific orientation, usually upright
    NEMA4 = outdoors and in any orientation
    NEMA4X= like NEMA4, but also rust proof

    Leave a comment:


  • bphgravity
    replied
    Check out Section 110.20 of the 2008 NEC. The enclosure-type numbers are from NEMA. The section and table was moved from 430.91 in the 2005 NEC.

    Leave a comment:


  • iwire
    replied
    You will only find NEMA references in Informational notes / Fine print notes which are not part of the code itself.

    Leave a comment:


  • danielbates7
    started a topic NEMA Enclosure

    NEMA Enclosure

    Hi Everyone,

    Dose anyone know where in the 2008 NEC it talks about NEMA in Enclosures and/or boxes? More specifically talking about NEMA boxes and motors.

    Thanks,